The report summary not displaying utilization ratio

Posted by  Dhanyaover 3 years ago
The report summary not displaying utilization ratio

Recently we have noticed that the report for anchor bolt design doesn't display utilization ratio at the summary on page 2, where as it is calculated as usual at the end of the page where combined check is done. In section 1.1 where summary of all load cases are given the utilization ratio appears as (infinity).

report,Profis Engineering,utilization ratio

1 Reply
Posted by Karan Khannaover 3 years ago
Hilti Verified

Hi Dhanya,

We have prepared a PROFIS model and found out model it shows the utilization summary on page no 2 of the report.
 
Our observation: the design report shared by the customer at page no 7 of the report it shows a steel strength capacity of rod 0.00 KN which is not the actual case. There is some value in the model which was not correct.

The model and report is attached for your reference.

Please feel free to reach out to us for more clarity.

Regards,
Team Ask Hilti SEA