Skip to main content
Cart

Engineer_Piping

Posted by Dodiek Sugiartoalmost 5 years ago
Engineer_Piping

Is there any for Hilti anchor with resistance at minus temp until -161 degree?

cryogenic,minus temperature

1 Reply
Posted by Reno Sorianoalmost 5 years ago

Hi Dodiek,

Thanks for raising your question on Ask Hilti!

Can you please provide us an idea of the specific application that you have that requires minus 161 degree Celsius?

Regards,

Ask Hilti Team
South East Asia

below zero,cold temperature

2 comments on this reply
Posted by  Notoalmost 5 years ago
Pak Dodiek explanation is correct. We need your advice the appropiate bolt to fix 1000mm width x 1000mm length x240 thickness of concrete block to the existing concrete wall 300 mm thickness. If you need further explanation please contact me by whatsapp on 6281313063456.

Posted by Dodiek Sugiartoalmost 5 years ago
Hi Hilti, This anchor will be used in area which is risk to get spill by LNG (temp LNG approx. -163 degree) And we have that requirement from owner Thank You Dodi