1,5 fire protection solutions for an electrical conduit

Posted by SARA MENENDEZalmost 3 years ago
1,5 fire protection solutions for an electrical conduit

Good morning,

I'm looking for a 1,5h fire-rated protection for an already-installed electrical conduit in a nuclear site. Please, could you provide guidance and technical specifications of products that could be installed (such as a kind of wrapping or a fire-rated shaft).

Thank you in advance,

nuclear,fire protection

1 Reply
Posted by Karan Khannaover 2 years ago
Hilti Verified

Hi Sara,

We would require more details to provide the solution or suggest any Firestop products. They have some parameters like Barrier type, type of wall/floor, opening size, electrical conduit material, Number of electrical conduits, etc.


For 1.5-hour F ratings in an electrical conduit case generally, concrete wall/floor we can suggest C-AJ-3095 which is with Hilti FS One Max intumescent sealant. We do not have a certificate with a particular 1.5-hour F-rating hence we are suggesting a 2-hour F-rating certificate. Further, this certificate does not cater to other attributes like movement capability in through penetration cases.

Note: Hilti products are designed for interior applications only. Our firestop sealant is not designed for exterior applications and has not been tested to the standards for exterior sealant/spray. 

Please feel free to reach out to us for any further clarification.

Regards,
Team Ask Hilti SEA